Wrong move. The wire is probably #4 which is only good to 80 amps. You need #2 for a 100 amp breaker. That is not the fix especially if it was running fine prior to the problem. You just created a fire hazard.

Put a 80 amp back in and find the real problem.
__________________


Three can keep a secret if two are dead.
Brian Oshman is online now   Reply With Quote
Old 15th June 2008, 10:33 AM   #22 (permalink)
Moderator Security
 
Natureboy's Avatar
 
Join Date: Dec 2004
Location: Canada, just north of 50
Posts: 2,813
Default Re: 818 shutting down

His wire on the secondary would be #6. On the primary he probably has #3. At least that is how I set up my UB's.

I think an 818 only draws like 68 amps on the secondary.

I still say it was just his original 80 amp breaker was weak. I have run them with 100 amp breakers before, but personally like Brian said, you should replace the 80 amp one with a new 80 amp one and see if it holds. The bed should not draw close enough to trip it unless something is wrong.
__________________

Original Tantoday Class of 2000! Tellin' it like it is.
www.millenniumtan.com
Natureboy is online now   Reply With Quote
Old 15th June 2008, 01:57 PM   #23 (permalink)
Super Star
 
Join Date: Jan 2005
Location: West Coast
Posts: 615
Default Re: 818 shutting down

I'll recheck the draw. I knew I'd read in the past natureboy had used 100's. I'll put in a new 80 and see what happens, just for safety sake.
coldgyn is online now   Reply With Quote
Old 15th June 2008, 02:54 PM   #24 (permalink)
Off The Chain Moderator
 
Brian Oshman's Avatar
 
Join Date: Nov 2004
Location: The Sun Doctor, Califon, NJ
Posts: 6,417
Default Re: 818 shutting down

The wire size determines the max breaker size. If you have #2 ran from the panel to the transformer then the 100 amp breaker is fine. If you have #4 ran then the 80 amp is the max breaker size.
__________________


Three can keep a secret if two are dead.
Brian Oshman is online now   Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 06:16 AM.
 
Copyright © 2008 by Virgo Publishing LLC, all rights reserved.
P.O. Box 40079, Phoenix, AZ 85067-0079
Phone: 480-990-1101 - Email: admin@tantoday.com
Privacy statement Terms of use