| Wrong move. The wire is probably #4 which is only good to 80 amps. You need #2 for a 100 amp breaker. That is not the fix especially if it was running fine prior to the problem. You just created a fire hazard. Put a 80 amp back in and find the real problem. |
| | |
| | #22 (permalink) |
| Moderator Security Join Date: Dec 2004 Location: Canada, just north of 50 Posts: 2,813 | His wire on the secondary would be #6. On the primary he probably has #3. At least that is how I set up my UB's. I think an 818 only draws like 68 amps on the secondary. I still say it was just his original 80 amp breaker was weak. I have run them with 100 amp breakers before, but personally like Brian said, you should replace the 80 amp one with a new 80 amp one and see if it holds. The bed should not draw close enough to trip it unless something is wrong. |
| | |
| | #24 (permalink) |
| Off The Chain Moderator Join Date: Nov 2004 Location: The Sun Doctor, Califon, NJ Posts: 6,417 | The wire size determines the max breaker size. If you have #2 ran from the panel to the transformer then the 100 amp breaker is fine. If you have #4 ran then the 80 amp is the max breaker size. |
| | |
![]() |