Default Re: 175 amp three phase

Quote:
Originally Posted by Bellastan View Post
I'm opening a hair salon with 3-4 tanning beds at open, I have an attached space with room to grow the tanning aspect(1000 sqf). The location has 6 tons of AC. I will phase in the tanning. I know I will need more electric down the road, allong with more AC. 75,000 people in 5 mile radius, Average income per person 60k. 95% white. hope that helps
I hope I get to Heaven too.
Mike_W is offline   Reply With Quote
Old 23rd May 2007, 11:57 PM   #22 (permalink)
Rookie
 
Join Date: Feb 2007
Location: colorado
Posts: 14
Default Re: 175 amp three phase

thanks again blond. I have been getting lots of mixed messages as far as the original question. Every one agrees that it can handle the three beds.(RIGHT?) The problem seems to be what else in the building is running off the electric, AC, light fixtures, clippers blowdryers you get the point. So the next question is how to figure what I really need to open. (300amp 400amp?) I realize some will think this is foolish, the tanning part is not what is paying the bills well maybe a couple . It is more of a marketing ploy to drive in more customers for hair services. I know I'm the black sheep on this forum since it will not be strictly a tanning salon but everyones input is greatly appreciated. Yeah I hope to see you in heaven. mikey Maybe you could make some use of yourself and give me some helpful information. not to start a pissing match but i have only seen a few post that were positive by YOU. However I am sure you have more knowledge about the industry than myself so maybe you could help a white man out in a 95% white area(80525,80528 zips)
Bellastan is offline   Reply With Quote
Old 24th May 2007, 12:38 AM   #23 (permalink)
Hall of Famer
 
blondjuls's Avatar
 
Join Date: Dec 2005
Location: US
Posts: 1,345
Default Re: 175 amp three phase

No problem Bella.

Fort Collins, nice place.

Here is a good site for you: Looks like its 85% white
http://www.city-data.com/city/Fort-C...-Colorado.html
__________________
"Courage, sacrifice, determination, commitment, integrity, heart, talent, guts, and beauty. To hell with sugar and spice. "
blondjuls is offline   Reply With Quote
Old 5th June 2007, 10:53 AM   #24 (permalink)
Hall of Famer
 
EliteMike's Avatar
 
Join Date: May 2007
Location: D.C.
Posts: 4,461
Send a message via AIM to EliteMike
Default Re: 175 amp three phase

I have to chime in here. You really need to be more specific as to what beds you are installing. My entry level beds only need a 20amp breaker and draws only 11-13 amps under load wired 3 phase

My midlevel requires a 30 amp breaker and only pulls 23-25 amps under load.

Is it possible to run 3 beds off what you have, YES it is. AC 60amps top for 6 tons, I'd probably say 40-50. Lights 20-40 amps, standard outlets 20-40 amps. water heater 30amps. You probably need dedicated circuits for emergency lighting and fire alarm. This excludes your hair dryers. These are typical breaker requirements. I couldn't tell you what the pull is on my double row of 4 lamp flouresent ceiling lighting, or what the draw is on my outlets. So yes, I think your 175 is okay, 200 would have been slightly better if 3 beds is all you will ever use.

Depending on where your incoming power is, you may want to consider an upgrade now. Certain areas do allow 2 services to be installed, although this is hard to come across. There was a local area around me that allowed it.

I have 600 amps and its just enough if everything was running in the building, although not enough for another AC unit.

AC is important, are you going to be able to vent your beds? some small beds can't be vented. Are your rooms going to be floor to ceiling, open ceiling, can you put a gap between the floor and the walls? Having the ability to circulate air can make a smaller unit much more effective. The radiant heat that comes from the canopy and bench is nothing compared to the heat that is exhausted. Most HVAC guys have no clue when it comes to tanning beds. You can literally heat your building with them unvented, why in the world they suggest some low powered units is beyond me.

If you are thinking about putting a large HP unit in and you think your rooms are large, go much bigger. I'm soo sorry we didn't make my HP room a few feet deeper.

Last edited by EliteMike : 5th June 2007 at 11:08 AM.
EliteMike is online now   Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is On
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 06:15 AM.
 
Copyright © 2008 by Virgo Publishing LLC, all rights reserved.
P.O. Box 40079, Phoenix, AZ 85067-0079
Phone: 480-990-1101 - Email: admin@tantoday.com
Privacy statement Terms of use